A power circuit breaker with integrated ground fault protection directly feeds a motor, the GF protection is performed by measuring the current of phase A, B and C, then calculating the vector sum in the electronic trip unit. If the vector sum exceeds the preset value, the breaker trips.
Sometimes nuisance trip occurs when the motor is starting. However, the insulation of cable and motor is verified good.
Current rating of the breaker is 630A, set value of GF protection is 0.2In=126A, time delay=0.2s. The trip event recorded in the datalog is I1:1838A, I2:1893A, I3:1885A, Ig:139A. (I1~I3: starting current, Ig:ground fault current).
The end user is doubting that the calculation accuracy of the trip unit is bad. I know the inrush current can cause spurious trip (because of DC component?). someone says it could be harmonics. But I don't think a motor itself is a big harmonic source. where does the residual current comes from and how to deal with it? Be grateful if you have any ideas.
Sometimes nuisance trip occurs when the motor is starting. However, the insulation of cable and motor is verified good.
Current rating of the breaker is 630A, set value of GF protection is 0.2In=126A, time delay=0.2s. The trip event recorded in the datalog is I1:1838A, I2:1893A, I3:1885A, Ig:139A. (I1~I3: starting current, Ig:ground fault current).
The end user is doubting that the calculation accuracy of the trip unit is bad. I know the inrush current can cause spurious trip (because of DC component?). someone says it could be harmonics. But I don't think a motor itself is a big harmonic source. where does the residual current comes from and how to deal with it? Be grateful if you have any ideas.