barrydmi
Member
- Location
- Washington
480 volt 3PH.600 amp type TJ G.E molded case circuit breaker with Microversa trip module, ground fault tripping capability. Trips now and again. 2 months may go by between tripping. No ground faults exist. At time of tripping, maybe 125 amps or less. Had breaker tested. Found to be in normal working order. 4 VFD's on line 1-10 horse power. G.E. tech says could be caused from harmonic build up on the line due to the non-linier loads, such as the VFD's. But 2 month's have gone by and it tripped again. Any help would be appreciated. Thank you. Barry.