Why does the code require separate automatic transfer switches (ATS) for emergency loads and non-emergency loads for general applications, but for healthcare you are allowed a single ATS for systems under 150 kVa? If I am remodeling a school that has a small generator (less than 150kVa) used only for life safety items such as emergency lighting and emergency egress, and they want to add a few receptacle circuits for their computer servers, then why is it required that I put them on separate ATS when healthcare allows it? It would seem to me that it should be completely opposite and healthcare should be separate no matter what? For reference (from the National Electrical Code Handbook 12th ed - M. Earley, et al): General Emergency Systems:
Article 700.5 (D):"Use. Transfer equipment shall supply only emergency loads."
Healthcare:Explanation: "Although the alternate power source for the emergency system is permitted to supply emergency loads as well as other loads, 700.5(D) limits the transfer switch to emergency loads, that is, loads classified as emergency in accordance with 700.1. Other loads, such as legally required standby loads or optional standby loads (covered by Articles 701 and 702), are not permitted to be supplied from the emergency system transfer switch. Where a single generator is used to supply both emergency and nonemergency loads, multiple transfer switches are required."
Article 517.30(B)(4): "Transfer Switches. The number of transfer switches to be used shall be based on reliability, design, and load considerations. Each branch of the emergency system and each equipment system shall have one or more transfer switches. One transfer switch shall be permitted to serve one or more branches or systems in a facility with a maximum demand on the essential electrical system of 150 kVA."
Explanation: "In larger health care facilities, the requirements of 700.5(D) and 517.30(B)(4) correlate from the perspective that there is o ne or more transfer switches that supply only emergency loads. However, 517.30(B)(4) also differs from 700.5 in smaller facilities with a maximum demand on the essential electrical system of 150 kVa or less. In those cases, a single transfer switch is permitted to supply the entire essential electrical system including loads that are not part of the emergency system. This is an example of where a requirement in Article 517 differs from a requirement in Article 700, and Article 517 takes precedence as is specified in 517.26."