kenaslan
Senior Member
- Location
- Billings MT
There has been some discussion here and there on the maximum number of bends in any conduit run. I believe that we all agree that it is 360 degrees or 4 quarter bends. The code states "There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes." IMO The definition of a "pull point" is a box or conduit body with a removable cover. No removable cover, no pull point. There are some that suggest the idea that you can unscrew a FLMC connector and pull the wire then put it back together again meets the intent of the code. I believe that is wrong. The amount of bends in the FLMC MUST be added to the conduit run in order to get the correct number of bends. Once a box or conduit body is encountered we restart the count toward 360 degrees again. Has anyone found a NEC definition for "Pull Point"? Anyone for the Code Panel have any insights? I have a "constructability manager" with the responsibility is to build it as cheap as possible. They believe that because "pull point" is not defined in the code, they can define it any way they want.