sfav8r
Senior Member
- Location
- San Francisco Bay Area
A friend is doing a kitchen remodel and has called me for information along the way. He just called for the inspection and failed due to "too many wires going through a single hole." and "Using a switch box as a junction box." First, for the second fail since I think its easy. The "switch box" the inspector is referring to is a 2 gang WP box (mulberry). He claims that is not a "junction box" that it is made for putting switches in and can't be used as a junction box. I have no idea what that's all about. However, the 2nd issue is that there are a number of cables (12/2, 14/2, 12.3 romex) exiting the box out a single 1" hole in the back of the box. The situation is that the box is fed with THHN via conduit and then spliced with Romex that runs out the back of the box and into the wall. He cited 310.15(b)(2)(a) stating that with that number of conductors they would have to be derated. I don't believe this is the case because the length is only an inch or two. I believe the 24" rule would apply and no derating is necessary. Having said that, I do believe he could have called the fact that the 1" clamp is almost certainly not rated for that number of conductors. I suppose the clamp could be removed and a busing installed instead and the romex could be stapled as it enters the house. Any thoughts?