Hi,
I am designing the electrical supply to an electric steam boiler of 1250 Kw, 380 Volts, 3 Phase, 60 Hz system
So,
FLA = 1899.23
The maximum size we use here usually is 600 MCM, thus, per Table 310.15(B)(16)
number of conductors per phase required is
1899.23/475 = 4
Since there are more than three current carrying conductors in a cable raceway or cable, in this case it's 4 X 3 = 12
per NEC Table 310.15(B)(3)(a), the derating factor would be 50%, so,
Ampacity = 1899.23/0.5 = 3798.46
Applying ambient temperature correction factor (considering ambient temperature of steam boiler room to be 50 C)
3798.46/0.82 = 4632
4632/475 =9.75
Per TABLE 250.122
Ground required would be 2 X 350 MCM
Thus,
the conductors required would be 10 of 600 MCM per phase. Or 40 conductors 600 MCM plus 2 X 350 MCM :jawdrop:
Do you agree with this?
I am designing the electrical supply to an electric steam boiler of 1250 Kw, 380 Volts, 3 Phase, 60 Hz system
So,
FLA = 1899.23
The maximum size we use here usually is 600 MCM, thus, per Table 310.15(B)(16)
number of conductors per phase required is
1899.23/475 = 4
Since there are more than three current carrying conductors in a cable raceway or cable, in this case it's 4 X 3 = 12
per NEC Table 310.15(B)(3)(a), the derating factor would be 50%, so,
Ampacity = 1899.23/0.5 = 3798.46
Applying ambient temperature correction factor (considering ambient temperature of steam boiler room to be 50 C)
3798.46/0.82 = 4632
4632/475 =9.75
Per TABLE 250.122
Ground required would be 2 X 350 MCM
Thus,
the conductors required would be 10 of 600 MCM per phase. Or 40 conductors 600 MCM plus 2 X 350 MCM :jawdrop:
Do you agree with this?