So what is the limit of conductors thru bored holes(300.4(A)(1)?
So what is the limit of conductors thru bored holes(300.4(A)(1)?
So what is the limit of conductors thru bored holes(300.4(A)(1)?
To expand on what User said what happens before and after the holes may trigger one of the other aspects of derating which is lack of spacing for more than 24". That is open to widely different interpretations.
Your veiw on this subject never ceases to confound me.
I cannot for understand why you feel, say five cables run through the same holes in row of studs for longer than 24" is not bundling. It clearly is bundled.
If it is harmful or not is another issue but they are bundled.
There is no limit. However the more conductors you run the higher any required ampacity adjustments become.
True except for when the cables are considered to be "bundled" for more then 24". Won't say this condition has never been debated here before though. Bottom line usually comes down to how the AHJ sees it though.Unless the holes are fire stopped, there would be no derating needed.
Your veiw on this subject never ceases to confound me.
I cannot for understand why you feel, say five cables run through the same holes in row of studs for longer than 24" is not bundling. It clearly is bundled.
If it is harmful or not is another issue but they are bundled.
My interpretation of 24" bundling: strapping together using tape, zip tie, tie wire or other means to hold cables together for longer than 24".
The problem is that opinions vary so when one is asked about defining bundling the answers will also vary. I tend to agree with you.
Laying them all in a corner at the bottom of a stud bay or on top of a top plate could, IMHO, also constitute bundling. But only the AHJ knows for sure. :happyyes:My interpretation of 24" bundling: strapping together using tape, zip tie, tie wire or other means to hold cables together for longer than 24".
You mean like this?
Is this bundling?
You mean like this:
But since they didn't secure them it made it easier to access that cable now didn't it?Full disclosure: The pics are NOT my install!
I had to do a few jobs at this house and had to be in the attic. The service was moved from the house to an added garage. Looked to be 50-60' from old location to the new.
They just draped the NM over the edge of the addition and along the bottom of the rafters.
One of the jobs was to find a short in an outside light. You will never guess which cable had the short!
Yep, one on the BOTTOM of the bundle/pile of NM!:rant:
But since they didn't secure them it made it easier to access that cable now didn't it?![]()