For residential installations, you will rarely have more than (1) ground rod. The concrete slab rebar should also be connected to the grounding system. This most often will meet the NEC requirement of 25 ohms or less.
But in industrial or manufacturing installations, there should be a ground loop or grid installed consisting of #4/0 or #2/0 grounding electrode conductors (GECs) with ground rods spaced every 50 to 100 feet. I typically space them every 35 feet or in the (4) corners of a ground loop if it is 50 ft x 50 ft or smaller. Structural steel, as well as the rebar in concrete foundations in an area should also be connected to comprise one continuous grounding system.
Places with sandy soils are about the only time one would need longer ground rods, or more frequently spaced ground rods along with ground enhancing material, due to the high insulating, low conductivity properties of sand, which equates to an increased resistance in the grounding system. Although, certain clients have stricter grounding requirements than others, which may require more or less depending on the client’s grounding specs/standards.
Respecrfully,
Christopher D. Staker, PE
Atlanta, GA