Number of Load Side Receptacles

Status
Not open for further replies.

A-1Sparky

Senior Member
Location
Vermont
Is there a code-mandated maximum number of receptacles that can be protected off the load side of a GFI? What about manufacturer recommended limits?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
There is no NEC maximum number of receptacles that are premitted to be installed downstream from a GFCI receptacle. You would need to follow the manufactures installation instructions (110.3(B)).