A A-1Sparky Senior Member Location Vermont Feb 5, 2009 #1 Is there a code-mandated maximum number of receptacles that can be protected off the load side of a GFI? What about manufacturer recommended limits?
Is there a code-mandated maximum number of receptacles that can be protected off the load side of a GFI? What about manufacturer recommended limits?
billsnuff Senior Member Location East of 480sparky Feb 5, 2009 #2 follow manufacturers recommendations IMHO, no NEC limit in resi, 180VA commercial, i think....
raider1 Senior Member Staff member Location Logan, Utah Feb 5, 2009 #3 There is no NEC maximum number of receptacles that are premitted to be installed downstream from a GFCI receptacle. You would need to follow the manufactures installation instructions (110.3(B)). Chris
There is no NEC maximum number of receptacles that are premitted to be installed downstream from a GFCI receptacle. You would need to follow the manufactures installation instructions (110.3(B)). Chris