Number of Outlets vs Overall Branch circuit Loads

aelec84

Member
Location
Los Angeles
Occupation
Electrical Engineer
Hello Forum,
Can you pls help demystify this?

Per NEC 13 outlets are permitted to be connected on a 20A branch circuit (almost 2400VA). But I have seen always load is limited to 16A/1920 VA in panel schedules (10 outlets). Where is the discrepancy?

Thank you.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Correct commercial buildings.
Not sure why they would limit the load to 16 amps. How do they know the actual load?

ecmweb_3356_503ecm31fig1.png
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I researched some more. Do you think its coming from 210.21 (B)(2) and 210.23(A)?
These are multi-receptacle circuits so I don't see where it would be required to calculate using 16 amp instead of 20 as in Mike's example. Where are you seeing the 16 amp number being used?
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
I could see someone treating those receptacle loads as continuous, thereby giving an 80% derate. I think this would be uncommon unless these serve a bunch of cubicle desks with a light, computer, monitor, etc that is on all day long. If these are general use circuits, I wouldn't expect the load to be continuous.

The 210.21(B)(2) limit is an 80% load limit at one receptacle, not the entire circuit.
 
Top