Can you pls help demystify this?
Per NEC 13 outlets are permitted to be connected on a 20A branch circuit (almost 2400VA). But I have seen always load is limited to 16A/1920 VA in panel schedules (10 outlets). Where is the discrepancy?
Thank you.
I researched some more. Do you think its coming from 210.21 (B)(2) and 210.23(A)?
These are multi-receptacle circuits so I don't see where it would be required to calculate using 16 amp instead of 20 as in Mike's example. Where are you seeing the 16 amp number being used?
I could see someone treating those receptacle loads as continuous, thereby giving an 80% derate. I think this would be uncommon unless these serve a bunch of cubicle desks with a light, computer, monitor, etc that is on all day long. If these are general use circuits, I wouldn't expect the load to be continuous.
The 210.21(B)(2) limit is an 80% load limit at one receptacle, not the entire circuit.