Hello!
We are using multiple Meanwell SE-450-12 power supplies on a project. From a system design standpoint, we're hoping to be able to power five of these power supplies from one 20A/110V circuit. The power supply data sheet says it has an inrush of 35A. Five of these would have a total inrush of 135A. Some of the equipment we are used to using says that the breaker can take 20X amp inrush, so up to 400A inrush on a 20A circuit. It's well documented and thus we can design with confidence.
On this current project, we're having a difficult time finding out what the power source is. We're trying to find out. We know it's a 20A/110V circuit, but we don't know the type of breaker, etc.
Assuming the breaker is a more typical 20A/110V breaker used for general facility lighting and such, would the inrush rating on this breaker be sufficient to run these 5 power supplies? I've been seeing numbers like 10X so up to 200A inrush. I would love to see a typical data sheet for a circuit breaker that shows something like inrush rating.
There are going to be 16 circuits, each potentially with 5 power supplies on each circuit. Would that have an impact on the main panel breaker?
Thanks for any direction and/or help you can provide.
We are using multiple Meanwell SE-450-12 power supplies on a project. From a system design standpoint, we're hoping to be able to power five of these power supplies from one 20A/110V circuit. The power supply data sheet says it has an inrush of 35A. Five of these would have a total inrush of 135A. Some of the equipment we are used to using says that the breaker can take 20X amp inrush, so up to 400A inrush on a 20A circuit. It's well documented and thus we can design with confidence.
On this current project, we're having a difficult time finding out what the power source is. We're trying to find out. We know it's a 20A/110V circuit, but we don't know the type of breaker, etc.
Assuming the breaker is a more typical 20A/110V breaker used for general facility lighting and such, would the inrush rating on this breaker be sufficient to run these 5 power supplies? I've been seeing numbers like 10X so up to 200A inrush. I would love to see a typical data sheet for a circuit breaker that shows something like inrush rating.
There are going to be 16 circuits, each potentially with 5 power supplies on each circuit. Would that have an impact on the main panel breaker?
Thanks for any direction and/or help you can provide.