nurse call wiring - required to be in conduit?

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
I don't believe nurse call wiring needs to be in conduit either by NEC nor by FGI or NPFA 99. I'm being challenged on this and wanted to make sure I've not missed something. Would appreciate your collective feedback.

Thanks,

Mike
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
See the last two paragraphs of 517.80

Roger
 