stevek220
New member
- san antonio, tx
Is it permissible to use HCF in a new nursing home for the rooms critical power plugs and lights ect?
Are you refering to health care facility otherwise known as hospital grade mc cable?
517.30 Essential Electrical Systems for Hospitals.
(C) Wiring Requirements.
(3) Mechanical Protection of the Emergency System.
The wiring of the emergency systems in hospitals shall be
mechanically protected. Where installed as branch circuits
in patient care areas, the installation shall comply with the
requirements of 517.13(A) and (B). The following wiring
methods shall be permitted:
(1) Nonflexible metal raceways, Type MI cable, or Schedule
80 PVC conduit. Nonmetallic raceways shall not be
used for branch circuits that supply patient care areas.
(2) Where encased in not less than 50 mm (2 in.) of concrete,
Schedule 40 PVC conduit, flexible nonmetallic or jacketed
metallic raceways, or jacketed metallic cable assemblies
listed for installation in concrete. Nonmetallic raceways
shall not be used for branch circuits that supply
patient care areas.
(3) Listed flexible metal raceways and listed metal sheathed
cable assemblies in any of the following:
a. Where used in listed prefabricated medical headwalls
b. In listed office furnishings
c. Where fished into existing walls or ceilings, not otherwise
accessible and not subject to physical damage
d. Where necessary for flexible connection to equipment
(4) Flexible power cords of appliances or other utilization
equipment connected to the emergency system.
(5) Cables for Class 2 or Class 3 systems permitted by Part
VI of this Article, with or without raceways.
I am not an expert
For critical power?
I am not an expert but wouldn't this apply?
Hospital. A building or portion thereof used on a 24-hour basis for the medical, psychiatric, obstetrical, or surgical care of four or more inpatients.
OP needs to further define what he means by "critical power"
From 517.2
Critical Branch. A subsystem of the emergency system
consisting of feeders and branch circuits supplying energy
to task illumination, special power circuits, and selected
receptacles serving areas and functions related to patient
care and that are connected to alternate power sources by
one or more transfer switches during interruption of normal
power source.
First off - he mentions this is a nursing home - the level of care given in this type of facility is usually just general care with maybe a limited number of areas with capability to support more advanced care - but usually only happens in rare cases.
What you quoted is for "Essential systems for Hospitals"
Is a nursing home a hospital?
Add: most resident rooms in nursing homes are just sleeping rooms and not even designated as patient care areas.
What they call critical care in a nursing home is more like general care in a hospital, and is typically temporary until the patient is transferred to a facility equipped to provide higher level of care.
Or because someone else is wrong.Honestly I feel like I am being given a hard time for bringing up something that if applies could cost the OP a ton of money to correct if it is ignored.
Everybody learns some thing when we log on here.
'Critical' is an NEC defined term, I assume if he used it he understands it but yes I agree he should clarify if he is using the term correctly.
The vagueness of the OP was likely why my post said 'Wouldn't this apply'
I think you are making huge assumptions, nursing homes can be from basic almost no care to full care.
Thanks, for telling me what I quoted.
It certainly can be, and if the OP is using the term critical power that suggests it is.
I agree.
I guess I am just not as familiar with all nursing homes across the US, I assume you must tour them regularly to make such sweeping statements.
Do I know this is a hospital? Heck no, but was I right to ask the question about 517.30? I think so.