NYC- Raised Floor Cabling

Status
Not open for further replies.

cdiangelo

Member
I have been told that in New York City I have to use rigid conduit in the raised floor plenum to run from the PDU to new outlets. Is this true? I have seen flexible cable whips under raised floors in NJ but I know NYC has some whacky rules.
 
Re: NYC- Raised Floor Cabling

NYC is under the 2002 NEC with a list of amendments under Local Law #81. The only amendment that I see is this:

645.5(D)(5)(c)-deleted reference to cable types NPLF and FPL.

So it would seem that all of the provisions of Article 645 in the 2002 NEC would apply to installations in NYC. Rigid conduit is permitted but not required. Here is the link to Local Law #81.

http://www.nyc.gov/html/dob/downloads/pdf/sec4a_ll_81_2003.pdf

[ June 13, 2005, 03:57 PM: Message edited by: infinity ]
 
Re: NYC- Raised Floor Cabling

From the original post I'm not sure this is a Article 645 area. Maybe they have admendments to article 300?

Steve
 
Re: NYC- Raised Floor Cabling

From the original post I'm not sure this is a Article 645 area. Maybe they have admendments to article 300?
Steve may be correct. I assumed that this was in a room covered under Article 645. It may or may not be. If it's not under 645 than 300.22(B) would apply. Local Law #81 does not change the requirements outlined in 300.22(B) with the exception of it including the words "fire rated spaces" in addition to the words ducts or plenums.

[ June 13, 2005, 04:41 PM: Message edited by: infinity ]
 
Re: NYC- Raised Floor Cabling

You do not have to use rigid. Many of the local union EC's require rigid, some engineering specs may require rigid, but no code requirement.
 
Re: NYC- Raised Floor Cabling

You do not have to use rigid. Many of the local union EC's require rigid, some engineering specs may require rigid, but no code requirement.
Why would an electrical contractor require the use of rigid conduit? Don't engineers usually spec the materials used? And who would pay for it? Seems like a much more expensive installation.
 
Re: NYC- Raised Floor Cabling

Originally posted by infinity:
Why would an electrical contractor require the use of rigid conduit?
To raise the price of the job.

Also to keep the workers off the bench.

Of course the reason given will be about quality and safety.
 
Re: NYC- Raised Floor Cabling

All is becoming clear...this would be union work in a data center in NYC. We are planning new work in an existing space that has rigid everywhere. I wanted to know where I stood before we put the SOW together. I was told that the maximum length that could be flexible was 6 feet.

Just to be more clear - we are adding new circuits to a data center with a raised floor. I have used the flexible ?bluish covered metal cable (Sealtite?))with an outlet at the end (L5-20), from the PDU in the room and left under the tile where the circuit was required. As you can guess I am not an electrician!

[ June 14, 2005, 09:44 AM: Message edited by: cdiangelo ]
 
Re: NYC- Raised Floor Cabling

Just curious, just because it is a data center does not mean article 645 applies. I have designed many a data centers and avoided 645 like the plague.
 
Re: NYC- Raised Floor Cabling

The floor plenum is strictly cooling and power cabling - there is no cable tray/raceway under the flooring. The whips would be left free and run to the new locations.
 
Re: NYC- Raised Floor Cabling

This may be your problem. You are limited in length as to the amount of flex cable that can be unsecured/unsupported. I think its 4', but would have to look it up and it may depend on which type of conduit.

In an NEC 645 area, you can have the flex conduits totally unsecured IF THEY ARE A UL LISTED ASSEMBLY. This was the killer for us. Our plant electricians can't do this, but an outside contractor can. Every time we use this contractor for this reason, the facilities electricians scream union busting. This approach may still not be satisfactory, as the practice of running power cords through a hole in the floor to a box on the concrete is discouraged. With listed DP power cords, you can do this. However, none of our computers come with DP stamped cords. So this forces you to mount the outlet box near the surface of the raised floor.

Our plant electricians use EMT under the floor with compression fittings and then use short whips of flex at the end to provide some choice as to where the outlet will actually be located. I like long runs of sealtite much better from an operations point of view.
 
Re: NYC- Raised Floor Cabling

All is becoming clear...this would be union work in a data center in NYC. We are planning new work in an existing space that has rigid everywhere.
When you say rigid are you saying threaded Aluminum or Galvanized Rigid Conduit? Or could it possibly be EMT?
 
Re: NYC- Raised Floor Cabling

I believe that it is all EMT...some is marked the rest really isn't. It is all compression fitted together and runs to wiring boxes. From there flexible BX? runs to the outlet boxes. The conduit is secured right to the subfloor.
 
Re: NYC- Raised Floor Cabling

Originally posted by cdiangelo:
The floor plenum is strictly cooling and power cabling - there is no cable tray/raceway under the flooring. The whips would be left free and run to the new locations.
Does not sound like a 645 application, so you cannot take advantage of the relaxed rules.
 