Re: NYC- Raised Floor Cabling
This may be your problem. You are limited in length as to the amount of flex cable that can be unsecured/unsupported. I think its 4', but would have to look it up and it may depend on which type of conduit.
In an NEC 645 area, you can have the flex conduits totally unsecured IF THEY ARE A UL LISTED ASSEMBLY. This was the killer for us. Our plant electricians can't do this, but an outside contractor can. Every time we use this contractor for this reason, the facilities electricians scream union busting. This approach may still not be satisfactory, as the practice of running power cords through a hole in the floor to a box on the concrete is discouraged. With listed DP power cords, you can do this. However, none of our computers come with DP stamped cords. So this forces you to mount the outlet box near the surface of the raised floor.
Our plant electricians use EMT under the floor with compression fittings and then use short whips of flex at the end to provide some choice as to where the outlet will actually be located. I like long runs of sealtite much better from an operations point of view.