We have an amendment allowing shunt trip button on a 1-2 family building. How can one achieve this ?
Let’s say 100 Amps for apartment 1 , 100 amps for apartment 2 and 100 amps for Public lights panel
Can shunt trip breakers be wired on load side ?
Are there 200 amp shunt trip breakers? Single phase 208v
Thank you
Section 230.85 – Add an Exception at the end of Section 230.85 to read as follows:
Exception: If the emergency disconnecting means cannot be located in a readily accessible
outdoor location, or if the utility metering equipment is located indoors, 1 of the following
disconnecting means shall be permitted:
1. A remote disconnecting means provided by the utility
2. An indoor shunt-trip disconnecting means with the control device located in a readily accessible outdoor location and marked, “Remote Emergency Disconnect”
3. An approved equivalent means.