You should not have any ferrous metal that completely encircles the Grounding Electrode Conductor. ...
A clarification would be the ferrous metal should not encircle the GEC in relatively close proximity and not be bonded to it.Don, I challenge your statement that ther should be no ferrous metal completely enclosing the GEC.
...
I should have added without bonding the ferrous metal to the GEC.Don, I challenge your statement that ther should be no ferrous metal completely enclosing the GEC.
I did cite 250.64(E) which addresses this.Running the GEC in steel pipe is a common practice, and I've often seen this specified by local ammendment. A GEC doesn't accomplish much after the lawnmower cuts it or the local copper thief removes it.
It's no issue 'bonding' the GEC at both ends; hardware is readily available for this purpose.
I have seen pictures of the damage where ferrous metal staps that completely encircled conductors of an "isolated phase" installation. The damage does not occur if you don't completely encircle the conductor. Same as when you cut slots in the ferrous enclosure between the entry points of isolated phases. 300.20As for the OP's concern ... I admit I never considered the possibility that a strut and strap together might create a 'complete encirclement' of the GEC. I can't say whether that's an issue or not; I've never encountered the situation.
The nylon bolts would completely prevent the damage or choke effect, assuming that there is no metal to metal contact.I suppose nylon bolts might help. I'd just as soon use a PVC strap with ordinary bolts into ordinary strut nuts. I'm not too happy clamping plastic with steel, fearing issues with abrasion and stress cracking of the PVC.