Re: o.k., so I'm a rookie......
You can use an earth ground resistance tester and perform a two-point test, this verifies continuity and will give you a reading and if everything is bonded, the reading would be less than .5 ohms maybe .25 ohms discounting lead contribution. You can also utilize a ducter/micro-ohm meter/DLRO, to perform this test.
Typically if this is in a commercial office building it is hard to be un-grounded, due to multiple paths. Building steel, water piping, metal studs, HVAC ducting, ECT. The real question is, is the low resistance path capable of carrying the fault current you going to impose on this path.