harrycan
Member
I am looking for direction on trying to elliminate about 7 amps of objectionable current on the secondary side grounding (building steel) conductor of a 75 kVA isolation (208 Delta-208/120 Wye) transformer.
Upon troubleshooting it was found that by opening the secondary side disconnect (3-pole) - current remained at 7 amps, while opening the primary side disconnect (3 pole) causes current to drop to zero. Why would this occur considering that in a normal grounding/bonding scenario the equipment (case) grounds, neutral, output ground through the conduit have the exact same path energized and de-energized. What is different in these two conditions (besides the transformer being energized) that would cause current to flow on the grounding wire?
Upon troubleshooting it was found that by opening the secondary side disconnect (3-pole) - current remained at 7 amps, while opening the primary side disconnect (3 pole) causes current to drop to zero. Why would this occur considering that in a normal grounding/bonding scenario the equipment (case) grounds, neutral, output ground through the conduit have the exact same path energized and de-energized. What is different in these two conditions (besides the transformer being energized) that would cause current to flow on the grounding wire?