Given:
Outside disconnect and main 'sub' panel properly wired.
GEC from the disco to the copper water lines entering the home. Not within the 5' rule but even if it was I would still see objectionable current at the test point.
The GEC run through a chase in the house and 'may' be the reason for the high EMF readings.
Assumption on my part: I believe that this bare wire may be coming in contact with the interior water lines that are also in this overhead chase prior to it's proper termination. Giving multiple parallel paths back to the source.
4.1 Amps measured at the pipe in the picture.
Now going outside, more than 10', and isolating the structure plumbing from the city plumbing should get rid of the reading.
My question is - Shouldn't there still be an objectionable current 'touch potential' present at this or any point on the plumbing system?
If so how does one solve this? Can't just not bond the interior metal water lines. Correct?
Outside disconnect and main 'sub' panel properly wired.
GEC from the disco to the copper water lines entering the home. Not within the 5' rule but even if it was I would still see objectionable current at the test point.
The GEC run through a chase in the house and 'may' be the reason for the high EMF readings.
Assumption on my part: I believe that this bare wire may be coming in contact with the interior water lines that are also in this overhead chase prior to it's proper termination. Giving multiple parallel paths back to the source.
4.1 Amps measured at the pipe in the picture.
Now going outside, more than 10', and isolating the structure plumbing from the city plumbing should get rid of the reading.
My question is - Shouldn't there still be an objectionable current 'touch potential' present at this or any point on the plumbing system?
If so how does one solve this? Can't just not bond the interior metal water lines. Correct?