Leespark57
Senior Member
- Location
- Boston, MA, USA
A colleague and I were having a discussion about using a metallic raceway between a meter socket and a main breaker panel. We both agree bonding bushings are required due to the fact there are service entrance conductors in the raceway. However, for example, a standard 200 amp meter socket has the neutral lug bonded to the frame of the enclosure of that meter socket. The 200 amp main panel also has the neutral connection bonded to the enclosure with the main bonding jumper. Therefore, using a metal raceway creates a parallel path for the neutral between the meter and the panel. Thus a percentage of the neutral current will be flowing through the raceway.
Isn't this considered objectionable current and a violation of 250.6?
Isn't this considered objectionable current and a violation of 250.6?