jdewitt37000
- Titusville, FL
- Electrical Contractor
Does article  250.142(B)(2) ex 2 allow 240.6 to be ignored or provide an exception to 240.6. I am having this discussion with someone whose knowledge of the code I have rarely questioned. This came up on set of plans that shows (4) services fed from a common gutter where the engineer shows a ground wire coming from the gutter to the meter enclosure (ME) and then down to the service disconnect (SD).
He says unequivocally 250.142(B)(2) ex 2 allows an exception to 240.6 at a service. I disagree, I believe it allows a grounding conductor from the load side of a service disconnect (SD) to either return from the SD through a raceway (or cable I suppose) and bond a meter enclosure if there is no other equipment grounding present at the enclosure (250.142(A). I don't believe it allows for the neutral bonded to the ME AND an equipment ground. from the load side of the disconnect.
When I mentioned 110.3(B) does not allow us to install an insulated neutral lug in a ME that did not come that way from the factory so I could comply with 240.6 he still said it meets code.
I don't understand what I am missing here.