With a large CT or clamp-on meter encompass all phase conductors and the neutral the reading should be ZERO "0". You can do this at every panel to locate the source of the problem I posted the information below previously.
? Perform zero sequence readings on each branch circuit (if possible) use a True RMS amp clamp and measure the phase/phase and grounded/neutral coonductors at the same time the circuits with any amperage are the culprits.
? Measure grounded/neutral conductor voltage at the panel (should be close to ?0? millivolts) circuits with any loads should have an increase in measured voltage (between the grounded/neutral conductor and the Equipment grounding conductor (copper conductor or conduit makes no difference). If the voltage is low, similar to the reading in the PDU, that is a suspect circuit.
? During a schedule outage turn off all the branch circuit breakers, unplug loads if possible and remove the grounded/neutral conductors from the neutral termination bar. Utilizing a low voltage megger 50VDC 0r 100 VDC (I use a low voltage megger to avoid damaging equipment with 500 or 1000 VDC meggers we normally use. The neutrals that megger bad, ?0? megohms, need to be traced out and the ?SHORTED? grounded/neutral conductor will need to be replaced, repaired, lifted depending on the exact nature of the problem.