Re: objectionable currents
One way to determine if current is flowing where it is not suppose to is by performing a simple test. Turn off all breakers leaving only the breakers on from one phase. Turn on all possible loads from that phase. Measure the current on the ungrounded conductor at the service, next measure the current on the service grounded neutral. They should be the same. If not, you have current flowing through another path or paths back to the source.
In all reality, if you are not having problems with your electrical system, and there are no signs or symptoms that point to current flowing on metal parts, you probably don't have a problem. All service enclosures and the grounding electrode system will have some current flow on them.