Mike Scarry
Member
- Location
- Roanoke, Virginia
I have a 208:480 delta:delta transformer, corner grounded, so this question doesn't really pertain to my current installation, but in going through Art. 250 I wondered: If I had a wye secondary with unbalanced phase loads, wouldn't objectionable neutral current flow through the XF case and on the EGC from the supply? Or is the idea that the neutral current is supposed to flow on the GEC for the separately derived system (the secondary) to the Grounding electrode? This doesn't seem right either, because then you would possibly have objectionable current on exposed structural steel, for example? Any insight as to what I am missing here would be greatly appreciated.