Sq D 999316 Replacement
There is no direct replacement breaker for this item
The 999316 is a 3 phase 100 amp 480 volt circuit breaker.
If you have to have NEW only, you can get some custom hardware made for approx $225.00 and install the current series.
Reconditioned is available but be careful. Most people only clean the exterior of the breaker and call it reconditioned. When we did reconditioning on these, they were very difficult because the arc chutes are several individual plate for each pole and there are springs that are in place for the tripping mechinism. Only buy these from a trusted reseller with alot of experience and request the test sheet with the thermal and instantaineous results.
We specialized in obsolete circuit breakers beginning in 1985 and are willing to give whatever information you may need. If you need specs on current series circuit breakers, the information is available on our website.
Sincerely Joe