Install concists of a motorized drapery controller mounted in a clothes closet. There are fuses inside the controller enclosure on the load side of the LV power supply.
So I told the contractor the controller cannot be located in the closet. 240.24(D)
I don't see anyway around this for him.
Question: Did I miss something that would allow this to remain???