wirebender Senior Member Location North Central Texas Oct 6, 2012 #1 Can I run the control wiring for ceiling mounted occupancy sensors and the lighting circuit conductors in the same conduit if I use 600v wire for both?
Can I run the control wiring for ceiling mounted occupancy sensors and the lighting circuit conductors in the same conduit if I use 600v wire for both?
R RUWired Senior Member Location Pa. Oct 7, 2012 #2 The sensor wiring is considered class 2 wiring and is not allowed in the same raceway or cable per 725.136
The sensor wiring is considered class 2 wiring and is not allowed in the same raceway or cable per 725.136