View attachment A9R3EF3.pdf
Please see attached. Here is my situation. These occupancy sensors have already been installed without a wall switch, but now the owner wants to be able to override the occupancy during good day light hours (of course right after drywall and ceiling grid). So I was wondering, instead of using the switch on the 120v circuit side (load side of occ sensor) can I switch the low voltage wire between the occupancy sensor and power pack? The switches will be located about 15 feet from the occupancy sensor (to much voltage drop?). The white wire would be the one to switch if possible, correct?
Thanks for the help.
Please see attached. Here is my situation. These occupancy sensors have already been installed without a wall switch, but now the owner wants to be able to override the occupancy during good day light hours (of course right after drywall and ceiling grid). So I was wondering, instead of using the switch on the 120v circuit side (load side of occ sensor) can I switch the low voltage wire between the occupancy sensor and power pack? The switches will be located about 15 feet from the occupancy sensor (to much voltage drop?). The white wire would be the one to switch if possible, correct?