Well, don't do that!Can anyone explain to me why it says to terminate the ground wire on the common screw?
Where is the pic now?Was gonna post a picture but there doesn't seem to be a way.
I see: "d. The sensor green wire will connect to the ground wire in the wallbox."It's for a 3 way occupancy sensor eaton os306u
This type of switch is what triggered the rule that the neutral conductor to be run to the switch locations. Most older electronic switches used the EGC as the neutral conductor to power the switch electronics. The exception to 404.2(C) only permits the use of the EGC as part of the power circuit for the internal electronics.I found it: "b. Connect the bare ground wire in the wallbox to the common terminal (usually a black screw or a marking such as COM or COMMON near the terminal) on the 3-way switch."
It doesn't compute, but that's under one specific switching situation, I'll have to look more to make sure it isn't an error.
402.2(C) ...The grounded conductor shall be extended to any switch location as necessary and shall be connected to switching devices that require line-to-neutral voltage to operate the electronics of the switch in the standby mode and shall meet the requirements of 404.22.
Exception:
The connection requirement shall not apply to replacement or retrofit switches installed in locations prior to local adoption of 404.2(C) and where the grounded conductor cannot be extended without removing finish materials. The number of electronic control switches on a branch circuit shall not exceed five, and the number connected to any feeder on the load side of a system or main bonding jumper shall not exceed 25. For the purpose of this exception, a neutral busbar, in compliance with 200.2(B) and to which a main or system bonding jumper is connected shall not be limited as to the number of electronic lighting control switches connected.
Yes, I get that. But why on earth does it say to wire it to the ground? The lutron I replaced it with didn't utilize the neutral at all. The secondary switch had basically two travelers terminated to the poles on the single pole switch. Idk man, either they messed up or they just have an impressively weird way of doing it. The sensor itself was not very good tbh. Just a warning to others to steer clear of Eaton occupancy sensors. View attachment 2573711