Joe Lancaster
Member
Is it a code violation to have breakers for A/C units in remote " panels", that exceed the equiptment "max overcurrent protection" rating as long as you have the proper size breakers at the "local disconnects".
Not at all. The wiring is protected and that is what matters. Of course the wire must be appropriately sized for the breaker at the panel to the disconnect.Is it a code violation to have breakers for A/C units in remote " panels", that exceed the equiptment "max overcurrent protection" rating as long as you have the proper size breakers at the "local disconnects".
Is it a code violation to have breakers for A/C units in remote " panels", that exceed the equiptment "max overcurrent protection" rating as long as you have the proper size breakers at the "local disconnects".
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
IMO, whether it goes through (1), (2), or infinty number of disconnects, the number still cannot be exceeded.
Even though it would not ever hurt anything, I don't think there are any exceptions that state if one correct sized breaker is used, the other can be oversized.
IMO, whether it goes through (1), (2), or infinty number of disconnects, the number still cannot be exceeded.
Even though it would not ever hurt anything, I don't think there are any exceptions that state if one correct sized breaker is used, the other can be oversized.
If the wire to the disco is properly sized then that is a feeder. The breaker at the disco protects the a/c- branch circuit. No problem. Of course, if the wire to the disco is not sized for the OCPD in the main panel then it is not okay.IMO, whether it goes through (1), (2), or infinty number of disconnects, the number still cannot be exceeded.
Even though it would not ever hurt anything, I don't think there are any exceptions that state if one correct sized breaker is used, the other can be oversized.
Is it a code violation to have breakers for A/C units in remote " panels", that exceed the equiptment "max overcurrent protection" rating as long as you have the proper size breakers at the "local disconnects".
IMO, whether it goes through (1), (2), or infinty number of disconnects, the number still cannot be exceeded.
Even though it would not ever hurt anything, I don't think there are any exceptions that state if one correct sized breaker is used, the other can be oversized.
If this was true, then even the main breaker in the panel would be wrong? or the breaker protecting a subpanel?