M mm Member Jul 4, 2004 #1 the question was, what is the max & min ocpd allowed for a non motor appliance : the appliance draws 20 amps at 120 volts
the question was, what is the max & min ocpd allowed for a non motor appliance : the appliance draws 20 amps at 120 volts
iwire Moderator Staff member Location Massachusetts Jul 4, 2004 #2 Re: ocp for a non motor applinnce ?exam question Assuming the OCP was not indicated on the appliance 20 min, 30 max. Take a look in Article 422
Re: ocp for a non motor applinnce ?exam question Assuming the OCP was not indicated on the appliance 20 min, 30 max. Take a look in Article 422