jeff43222
Senior Member
- Location
- Minneapolis, Minnesota
I had a guy call me today about doing various wiring tasks around his house, and one thing he wants me to do is wire up some receptacles for his table saw and planer. Since I like to follow 110.3(B), I asked to see the instructions that accompanied the tools. The table saw called for not less than #10 wire and protection with a 40A time lag fuse. The planer called for not less than #12 wire and a 20A time lag fuse. Both tools' nameplates listed single phase, 15A, 230V. Both also came with cord-n-plug installed.
My impression is that I must install fuse boxes specifically for this installation and cannot substitute circuit breakers. I don't get a lot of calls for wiring up tools with motors and want to be sure I do this right.
My impression is that I must install fuse boxes specifically for this installation and cannot substitute circuit breakers. I don't get a lot of calls for wiring up tools with motors and want to be sure I do this right.