gepman
Member
- Location
- California
Situation
Generator with 125/2 CB feeding through 100A unfused disconnect to "emergency" side of 100A ATS. 100/2 CB feeding through 100A unfused disconnect to "normal" side of 100A ATS. "Common" side of ATS connected to panelboard with 100/2 main CB.
Question
What is the required OCP for the ATS (i.e. what size CB is required at the generator)?
From my reading of Article 240, it applies only to conductors. Table 240.3 describes which articles apply to OCP for equipment which I assume an ATS is categorized as. I looked in article 445 (generators), articles 700, 701, and 702 (emergency and standby systems), and even article 404 (switches). None had any OCP requirements.
Is there any article which gives requirements for OCP for ATS's, switches, or other equipment not listed in Table 240.3? Is there any article which gives sizing requirements (i.e. equipment rating must be greater than the calculated load) for ATS's, switches, or other equipment not listed in Table 240.3. The closest that I could come is 110.3(A)(7) and perhaps 110.3(B).
I am not that interested in opinions on the safety of the above scenario. I am interested in the exact article number that gives the requirements. I have referenced the 2008 NEC. If replying with any other edition of the NEC, please state the year.
Generator with 125/2 CB feeding through 100A unfused disconnect to "emergency" side of 100A ATS. 100/2 CB feeding through 100A unfused disconnect to "normal" side of 100A ATS. "Common" side of ATS connected to panelboard with 100/2 main CB.
Question
What is the required OCP for the ATS (i.e. what size CB is required at the generator)?
From my reading of Article 240, it applies only to conductors. Table 240.3 describes which articles apply to OCP for equipment which I assume an ATS is categorized as. I looked in article 445 (generators), articles 700, 701, and 702 (emergency and standby systems), and even article 404 (switches). None had any OCP requirements.
Is there any article which gives requirements for OCP for ATS's, switches, or other equipment not listed in Table 240.3? Is there any article which gives sizing requirements (i.e. equipment rating must be greater than the calculated load) for ATS's, switches, or other equipment not listed in Table 240.3. The closest that I could come is 110.3(A)(7) and perhaps 110.3(B).
I am not that interested in opinions on the safety of the above scenario. I am interested in the exact article number that gives the requirements. I have referenced the 2008 NEC. If replying with any other edition of the NEC, please state the year.