Is the following installation a NEC violation of 240.4 (B) (3).
A 13.8kv fused primary, 750 kva transformer, has a 480/ 277 3 phase secondary, with a 1200 amp frame / 1200 amp trip main breaker feeding a distribution bus. I am thinking it should be a 1000kva transformer to comply with Table 450.3(A) Thanks
A 13.8kv fused primary, 750 kva transformer, has a 480/ 277 3 phase secondary, with a 1200 amp frame / 1200 amp trip main breaker feeding a distribution bus. I am thinking it should be a 1000kva transformer to comply with Table 450.3(A) Thanks