We have a 34.5 kV Utility Source feeding a customer-owned 34.5kV: 480Y/277V, 500 KVA padmount, which in turn directly feeds a 480V: 208Y/120V, 225 kVA Dry-type Transformer. (We could not find a 34.5kV: 208Y/120V padmount in time). The 208Y/120V secondary will supply an office building/warehouse for a Data Center. There are no loads between the two transformers, which are located around 8 ft apart. Two questions:
1) If the Utility OH line tap is protected with fuses, and the padmount has primary fuses, where is OCPD required between the transformers?
2) If a 480V Breaker is used ahead of the Dry-type, is this where the Main Bonding Jumper should exist? I'm confused as to what is considered "Service Disconnect" in this situation.