I just read our patron's article called "Conductor Sizing and the National Electrical Code". The link is: http://www.mikeholt.com/technical.php?id=nec/unformatted/necconductorsizing&type=u&title=Conductor%20Sizing%20and%20the%20National%20Electrical%20Code
I thought I understood this topic well, but now I'm confused. Please help me with an example calculation:
Suppose you had to find the correct OCPD and Cu THHN feeder conductors to be run in conduit for a 4-Wire 3-Phase Wye 75C panelboard with a continuous 190 Amp load at an ambient of 30C.
</font>
I thought I understood this topic well, but now I'm confused. Please help me with an example calculation:
Suppose you had to find the correct OCPD and Cu THHN feeder conductors to be run in conduit for a 4-Wire 3-Phase Wye 75C panelboard with a continuous 190 Amp load at an ambient of 30C.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Under 215-3 and 384-16(d), the OCPD must be at least 1.25 x 190 Amps = 238 Amps. From the standard CB ratings in 240-6, the minimum OCPD is 250 Amps.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Under 215-2, the conductors must also be rated for at least 238 Amps, and under 110-14(c), the 75C conductor rating must be used. So table 310-16 gives a conductor size of 250 MCM with a 75C rating of 255 Amps.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">As we have 4 current-carrying conductors in the pipe, we have to derate the ampacity using table 310-15(b)(a)(2). Under 110-14(c), we use the 90C rating for this, so the 250 MCM is derated to 290 Amps x 0.8 = 232 Amps.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Under 240-3(b), we can use the next larger standard OCPD to protect the 250 MCM, which is 250 Amps. And this satisfies the minimum OCPD required for the load.</font>