Hello Folks,
I need to feed a temporary chiller load. Unfortunately, I don't have direct 460V supply available, so I am exploring to get a 25kV/460V step down transformer to feed the load. I am wondering with following and would appreciate if anyone can provide some answer.
1-Do I need breaker protection at primary and secondary of transformer too, or only primary protection is enough?
2- As per NEC450.3, I guess, it will be unsupervised area, and impedance might be around 6%, so I need to have 600% rating of breaker or 300% rating of fuse to feed the primary of the transformer?
3- If I am using breaker, what setting I should use to set the breaker at? Long time should be 125% and Short time 600%. Is that acceptable to protect conductors?
4- I am sure rental chiller will have protection, so I would imagine the CB/ Fuse protection should be 125% since it will be less than 600V.
5- Cable sizing would be done as per NEC code, 125% primary and secondary. Correct?
I need to feed a temporary chiller load. Unfortunately, I don't have direct 460V supply available, so I am exploring to get a 25kV/460V step down transformer to feed the load. I am wondering with following and would appreciate if anyone can provide some answer.
1-Do I need breaker protection at primary and secondary of transformer too, or only primary protection is enough?
2- As per NEC450.3, I guess, it will be unsupervised area, and impedance might be around 6%, so I need to have 600% rating of breaker or 300% rating of fuse to feed the primary of the transformer?
3- If I am using breaker, what setting I should use to set the breaker at? Long time should be 125% and Short time 600%. Is that acceptable to protect conductors?
4- I am sure rental chiller will have protection, so I would imagine the CB/ Fuse protection should be 125% since it will be less than 600V.
5- Cable sizing would be done as per NEC code, 125% primary and secondary. Correct?