acoron01
Member
- Location
- Albuquerque, N.M., USA
Hello,
i would like some advice/direction as to whether our main OCPD for our secondary side of our transformer is sized correctly. I do not think it is protecting the equipment. We have a , 480V, 225kva, 3 Phase westinghouse transformer with the sub panel in the secondary side of the transformer. There are 6 feet of parrallel 4/0 feeding the backfed main in the subpanel. The main is a cuttler hammer KD3400F breaker. I did a quick calc, to size the breaker correctly and came up with 270Amps available from the secondary side, with a 250Amp breaker, 4-250kcmil conductors & 1-#2AWG EGC rated at 75 degree C. The available short current at a 4.14% Z was 6.5KA. The existing configuration is a 400 amp main, with 6 feet of parrallel 4/0, and 1-4/0 EGC.
i would like some advice/direction as to whether our main OCPD for our secondary side of our transformer is sized correctly. I do not think it is protecting the equipment. We have a , 480V, 225kva, 3 Phase westinghouse transformer with the sub panel in the secondary side of the transformer. There are 6 feet of parrallel 4/0 feeding the backfed main in the subpanel. The main is a cuttler hammer KD3400F breaker. I did a quick calc, to size the breaker correctly and came up with 270Amps available from the secondary side, with a 250Amp breaker, 4-250kcmil conductors & 1-#2AWG EGC rated at 75 degree C. The available short current at a 4.14% Z was 6.5KA. The existing configuration is a 400 amp main, with 6 feet of parrallel 4/0, and 1-4/0 EGC.