OCPD for multimotor AC equipment

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
How do you interpret 440.22(B)(1):

Where a hermetic refrigerant motor-compressor is the largest load connected to the circuit, the rating or setting of the branch-circuit short-circuit and ground-fault protective device shall not exceed the value specified in 440.22(A) for the largest motor-compressor plus the sum of the rated-load current or branch-circuit selection current, whichever is greater, of the other motor-compressor(s) and the ratings of the other loads supplied.

I can interpret this two ways:

1) Not to exceed the largest compressor RLA (175% - 225% round down) then add remaining RLA then round down.

Example:

49.6A compressor RLA
9.2A fan motor RLA

49.6 x 1.75 = 86.8A , round down = 80A + 9.2A = 89.2 round down = 80A

OR

2) Not to exceed largest compressor RLA (175% - 225%) + remaining RLA then round down.

49.6 x 1.75 + 9.2 = 96A round down = 90A

Thanks
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
How do you interpret 440.22(B)(1):

Where a hermetic refrigerant motor-compressor is the largest load connected to the circuit, the rating or setting of the branch-circuit short-circuit and ground-fault protective device shall not exceed the value specified in 440.22(A) for the largest motor-compressor plus the sum of the rated-load current or branch-circuit selection current, whichever is greater, of the other motor-compressor(s) and the ratings of the other loads supplied.

I can interpret this two ways:

1) Not to exceed the largest compressor RLA (175% - 225% round down) then add remaining RLA then round down.

Example:

49.6A compressor RLA
9.2A fan motor RLA

49.6 x 1.75 = 86.8A , round down = 80A + 9.2A = 89.2 round down = 80A

OR

2) Not to exceed largest compressor RLA (175% - 225%) + remaining RLA then round down.

49.6 x 1.75 + 9.2 = 96A round down = 90A

Thanks

Look to the manufacturer's installation manual, since their recommendations take into consideration the advantage of the suction return to cool the motor windings.
 

cppoly

Senior Member
Location
New York
Thanks.

Sometimes manufacturer's get it wrong on their spec sheet so you have to calculate the value yourself.

440.22(B)(1) seems ambiguous though.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
That's reason the manufacturer's Installation Manual recommended MCA do not match the manual calculations.
 