How do you interpret 440.22(B)(1):
Where a hermetic refrigerant motor-compressor is the largest load connected to the circuit, the rating or setting of the branch-circuit short-circuit and ground-fault protective device shall not exceed the value specified in 440.22(A) for the largest motor-compressor plus the sum of the rated-load current or branch-circuit selection current, whichever is greater, of the other motor-compressor(s) and the ratings of the other loads supplied.
I can interpret this two ways:
1) Not to exceed the largest compressor RLA (175% - 225% round down) then add remaining RLA then round down.
Example:
49.6A compressor RLA
9.2A fan motor RLA
49.6 x 1.75 = 86.8A , round down = 80A + 9.2A = 89.2 round down = 80A
OR
2) Not to exceed largest compressor RLA (175% - 225%) + remaining RLA then round down.
49.6 x 1.75 + 9.2 = 96A round down = 90A
Thanks
Where a hermetic refrigerant motor-compressor is the largest load connected to the circuit, the rating or setting of the branch-circuit short-circuit and ground-fault protective device shall not exceed the value specified in 440.22(A) for the largest motor-compressor plus the sum of the rated-load current or branch-circuit selection current, whichever is greater, of the other motor-compressor(s) and the ratings of the other loads supplied.
I can interpret this two ways:
1) Not to exceed the largest compressor RLA (175% - 225% round down) then add remaining RLA then round down.
Example:
49.6A compressor RLA
9.2A fan motor RLA
49.6 x 1.75 = 86.8A , round down = 80A + 9.2A = 89.2 round down = 80A
OR
2) Not to exceed largest compressor RLA (175% - 225%) + remaining RLA then round down.
49.6 x 1.75 + 9.2 = 96A round down = 90A