I went through this thread from awhile back:
My question is regarding Post #16 (in bold here):
430.62(A): The maximum permitted OCPD for the 24.4A compressor is 60A...plus the sum of the full load currents of the other motors.
Edit: I forgot the other motors in the first unit however:
60+1.7+6.9+4(33)=200.6. A 200A breaker with an MCA of 171.1.
I follow everything except for the value of 60 amps. 430.62(A) states that for compressors, you refer to 440.22(A)... 440.22(A) states not to exceed a max of 225% for single compressors. 24.4 amps, which the RLA for one compressor, x 2.25 = 54.9. Then you round down to a 50 amp breaker, since you can't exceed 54.9 amps.
So shouldn't the math be 50+1.7+6.9+4(33) = 190.6? Hence the breaker size for the feeder serving all the AC units is 175 amps.
Subpanel size for 5 HVAC units
Hello, i want to make sure i got this correct. We are bidding job for hvac and electrical. The hvac will need a subpanel installed. The name plate says min circuit ampacity is 40 amps and the max breaker size is 60 amps. I am thinking we need a 300 amp sub panel 60*5=300 or a 320 amp sub panel...
forums.mikeholt.com
My question is regarding Post #16 (in bold here):
430.62(A): The maximum permitted OCPD for the 24.4A compressor is 60A...plus the sum of the full load currents of the other motors.
Edit: I forgot the other motors in the first unit however:
60+1.7+6.9+4(33)=200.6. A 200A breaker with an MCA of 171.1.
I follow everything except for the value of 60 amps. 430.62(A) states that for compressors, you refer to 440.22(A)... 440.22(A) states not to exceed a max of 225% for single compressors. 24.4 amps, which the RLA for one compressor, x 2.25 = 54.9. Then you round down to a 50 amp breaker, since you can't exceed 54.9 amps.
So shouldn't the math be 50+1.7+6.9+4(33) = 190.6? Hence the breaker size for the feeder serving all the AC units is 175 amps.