Equipment involved is an Isolation transformer/power center, rated at 10kva at 208/230v 1ph.
There is a main cb rated at 60amps ahead of the transformer incorporated into the equipment.
I am just trying to determine the maximum size OCPD for the feeder to this equipment so that the upstream OCPD does not trip before the equipment main
OCPD.
OK Per 450.3(b)
The 60 amp OCPD installed ahead of the transformer it seems to me is sized to protect the secondary since it is rated at 125%.
The primary can be rated at 250% or @ 100amp. I can install a 100 amp OCPD ahead of the feeder to this.
Am I looking at this correctly?
Thanks for any input.