Is a branch circuit OCPD for two pumps (fed through a controller) sized differently depending on whether the pumps start at the same time or not? Because I can’t find this requirement in 430.53.
For instance, if you have two sump pumps that do not start at the same time that are 208V, 3 phase, 1 HP (4.6 FLC), the OCPD should be sized 2.5 x 4.6 = 15 AMP OCPD + 4.6 amps = 15 AMP OPCD (round down). If they start at the same time I would think the OCPD would be 4.6x2 = 9.2 amps x 2.5 = 23 amps = 20 amps OCPD.
Thoughts?
For instance, if you have two sump pumps that do not start at the same time that are 208V, 3 phase, 1 HP (4.6 FLC), the OCPD should be sized 2.5 x 4.6 = 15 AMP OCPD + 4.6 amps = 15 AMP OPCD (round down). If they start at the same time I would think the OCPD would be 4.6x2 = 9.2 amps x 2.5 = 23 amps = 20 amps OCPD.
Thoughts?