I am looking at an application where there is a VFD fed from a panelboard with a 60A breaker and #10 wire. The motor fed from the VFD is a 15hp motor with a 21A FLA rating.
In this applicaiton would the #10 cable be considered a motor feeder circuit or branch circuit?
If it is a branch circuit I'm thinking the #10 wire is adequatly protected by the 60A breaker since the NEC allows branch circuit breaker to be 250% of motor FLA. However if this is considered a feeder circuit I dont think the #10 wire is adequatly protected by the 60A breaker. Im not sure of the VFD input requirments for feeder ampacity of max OCPD size but regardless of what the VFD required the amapcity of the feeder circuit would still have to be adequate for the feeder breaker correct?
The only other thing that comes to mind is if the VFD has a main breaker rated at 30A which could then utilize the tap rule and protect the #10 cable however I dont see why the VFD would have a 30A breaker and the feeder breaker be a 60A breaker.
Any thoughts?
In this applicaiton would the #10 cable be considered a motor feeder circuit or branch circuit?
If it is a branch circuit I'm thinking the #10 wire is adequatly protected by the 60A breaker since the NEC allows branch circuit breaker to be 250% of motor FLA. However if this is considered a feeder circuit I dont think the #10 wire is adequatly protected by the 60A breaker. Im not sure of the VFD input requirments for feeder ampacity of max OCPD size but regardless of what the VFD required the amapcity of the feeder circuit would still have to be adequate for the feeder breaker correct?
The only other thing that comes to mind is if the VFD has a main breaker rated at 30A which could then utilize the tap rule and protect the #10 cable however I dont see why the VFD would have a 30A breaker and the feeder breaker be a 60A breaker.
Any thoughts?