Why the 0.8, do you have two sets of CCCs in each conduit?Terminal 75°
Wire Rating 90°
Amb. Temp 0.91
No. CCC 0.80
500kcmil @ 75° 380A
500kcmil @ 90° 430A
Current = 1205A (continuous load)
That check is correct only for 100% rated OCPD. Otherwise this check gets a 125% factor.500kcmil 75°
380A > 376.6A ; OK
That check is OK for the current, but not for the OCPD as per above.500kcmil 90°
430A x 0.91 x 0.80 > 301.25A
313A > 301.25A; OK
Thank you WayneWhy the 0.8, do you have two sets of CCCs in each conduit?
Based on the above, if your OCPD is not 100% rated, it has to be at least 1506A, so apparently 1600A if that is the next size up available to you. Because of 240.4, and 240.4(B)'s non-applicability over 800A, that means your ampacity actually has to be at least 1600A, or 400A per set.
400A / 0.91 / 0.8 = 549A. So each set would need to be at least 800 kcmil Cu for 90C rated insulation.
Obviously if you can change some of the variables in your favor, you can get the conductor size down. E.g. more sets, only 3 CCCs, reduce the continuous current to be only 1200A so you can use a 1500A OCPD, or use a 100% rated OCPD.
That check is correct only for 100% rated OCPD. Otherwise this check gets a 125% factor.
That check is OK for the current, but not for the OCPD as per above.
Cheers, Wayne
one set one conduit but i count N as CCCs as there's are comms connecting to Neutral and provision if for future circuit using Neutral on the load centerWhy the 0.8, do you have two sets of CCCs in each conduit?
You almost never have to count N as a CCC when it is accompanied by a balanced set of ungrounded conductors. In the 2017 NEC, this is 310.15(B)(5). So you do not need the ampacity adjustment factor of 0.8.one set one conduit but i count N as CCCs as there's are comms connecting to Neutral and provision if for future circuit using Neutral on the load center
got it. thank youYou almost never have to count N as a CCC when it is accompanied by a balanced set of ungrounded conductors. In the 2017 NEC, this is 310.15(B)(5). So you do not need the ampacity adjustment factor of 0.8.
For a brief explanation, consider a set of resistive loads all connected L-N across the 3 different ungrounded conductors (for the case of 3 phase) and suppose the load is a maximum of 100A on any ungrounded conductor. One possible value of the currents (L1,L2,L3,N) is (100,100,100,0), where you have maximum load on each ungrounded conductor. The currents on N add to zero as the contribution from the 3 ungrounded conductors are pairwise 120 degrees out of phase.
This is the worst case heating you can get in the conductors subject to the 100A load limit. If you decrease the current in any one of the ungrounded conductors, current in N will go up accordingly. But as the heating varies as the square of the current, the total heating will actually be less.
Cheers, Wayne