OCPD new service

Status
Not open for further replies.

Designer69

Senior Member
From what I've been able to dig up.. an OCPD is not required in this situation. (See pic)

But if asked why is it not required there. Would the correct answer be...

"Transformer secondary protection is not required for the following conditions:

"For transformers with primary voltage greater than 1,000V at supervised locations, with the following maximum primary protection [Table 450.3(A)]:"

Untitled.jpg
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Often the service transformer is under POCO jurisdiction and NEC doesn't apply.
The diagram you show seems to fall under 230.31 and 230.71
 

kwired

Electron manager
Location
NE Nebraska
I agree with Augie so far.

Is the conductors in question "service conductors" or is it secondary conductors of a "separately derived system"?

The note on that drawing doesn't go with the situation if they are indeed "service conductors".

If it is transformer secondary conductors (separately derived system), I'd have to dig a little deeper to verify what that note says. I'm fairly certain it is allowed like shown for secondary under 1000 volts with some conditions - basically feeder tap rules in 240.21.
 

Designer69

Senior Member
I agree with Augie so far.

Is the conductors in question "service conductors" or is it secondary conductors of a "separately derived system"?

Service Conductors.


Is there any section in the code that states that the OCPD ahead of the wireway is basically not required?

Thank You
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The rules in Article 450 only apply to the protection of the transformer itself, they do not cover the protection of the transformer conductors.
 

kwired

Electron manager
Location
NE Nebraska
The rules in Article 450 only apply to the protection of the transformer itself, they do not cover the protection of the transformer conductors.
If the conductors in question are service conductors, which OP says they are, the transformer is POCO equipment and not covered by NEC.
 

kwired

Electron manager
Location
NE Nebraska
Service Conductors.


Is there any section in the code that states that the OCPD ahead of the wireway is basically not required?

Thank You
No. If you put OCCPD ahead of the wireway - that OCPD becomes the service disconnecting means and there conductors in the wireway are no longer service conductors.

Multiple service disconnecting means are allowed - general rule is up to six. Setup with wireway like in your picture is a common method of installing multiple disconnects for a single service.
 