OCPD on 24V side for 1000VA transformer

Status
Not open for further replies.

victor.cherkashi

Senior Member
Location
NYC, NY
Turnstile’s manufacturer provides 1000VA, 1-phase, 120V/24V transformer to power several turnstiles. Transformer installed 70ft away from turnstiles. I got wiring diagrams for review from Turnstile’s contractor, but there was no OCPD on 24Volt side. Diagram shows two circuits on 24V side (3#12AWG each). To my question why there is no OCPD, they said we never saw OCPD devices installed on 24V side.

I requested to install 20A breaker for each 3#12AWG circuit on 24V side. Since it is not circuit class 1,2,3 I applied standard rules as for 120V, 208V, 480V etc.

Just want to hear your opinions, maybe I missed something in NEC.
 
If this a 2 wire 24 volt secondary the primary OCPD can also protect the secondary and conductors as long as it is sized correctly.
Edit to add: Just noticed you said 2 #12 circuits. The output of the transformer is about 42 amps. The #12s will need OC protection.
 
If this a 2 wire 24 volt secondary the primary OCPD can also protect the secondary and conductors as long as it is sized correctly.
Edit to add: Just noticed you said 2 #12 circuits. The output of the transformer is about 42 amps. The #12s will need OC protection.
There will be 20A OCPD on primary. Ratio is 120/20=5.

20Amp*5=100A

Per my understanding they need to install 100A rated wires on 24V side to get away with OCPD on 24V side of the transformer.
 
There will be 20A OCPD on primary. Ratio is 120/20=5.

20Amp*5=100A

Per my understanding they need to install 100A rated wires on 24V side to get away with OCPD on 24V side of the transformer.
I don't see how that complies with Table 450.3(B) as that is above 167% of the primary current and the use of a a primary OCPD that exceeds 13.91 amps requires that the transformer have secondary OCPD. Note that there is no "round-up" note for the primary protect in the less than 9 amp column.
 