industrial1003
Member
- Location
- Easton Pennsylvania
I have a unique piece of metal forming equipment that has it's own supply conductor OCPD in the form of a fused disconnect switch for the machine. The machine was built for later expansion if needed so the disconnect switch is oversized and using UL listed fuse reducers (100A switch with 50A fuses). Can I wire this to a 100A breaker in my panelboard as long as the conductors supplying the machine are rated for the 100A breaker after the required derating? It would save time if the machine is expanded down the road. Also, am I correct in assuming the breaker in question is considered a feeder OCPD since the fuses at the machine disconnect would be considered the branch OCPD?
We run into a lot of this in our facility as we use modular equipment, and most is overbuilt. Any help would be appreciated.