Have some large feeders(load side) running from distribution gear in one building in duct banks( about 200') to another building where we are intercepting existing risers in a splice box(#500 mcm). Would any OCPD be required in the new building near the splices or the distribution gear is fine? Thanks.
 
Have some large feeders(load side) running from distribution gear in one building in duct banks( about 200') to another building where we are intercepting existing risers in a splice box(#500 mcm). Would any OCPD be required in the new building near the splices or the distribution gear is fine? Thanks.

As long as they are not taps, you do not need another OCPD. You might need a disconnect however.
 