Hello everyone, I'm reviewing a one-line diagram and I am a little confused on what size OCPD might be necessary for a conductor of 840 ampacity. I'm looking at two sets of 3#600mcm running from a chosen 800A fuse to a new switchboard. Referring to NEC 2008, I am stuck in a gray area between 240.4(B) and 240.4(C). A 1000A fuse would not be acceptable because that would go against 240(C), but we can't use the chosen 800A fuse because that would go against the guidelines of 240.4(B)(3). Would the only solution be resizing the conductors? Thank you.